貌似电击防护归根结底就是欧姆定律,电阻串并联。接触电压、电流计算{:4_118:}
尺短寸长
发表于 2014-3-5 10:26:54
回复 496# 北方郎
老诚嗤之以鼻:初中生读一遍都过分。{:sweat:}
rainmen_73
发表于 2014-3-5 10:30:30
TT制的安全性必须基于RCD的可靠动作。RCD故障时的人身安全如何考虑,我的想法还是每个路灯设两圈等电位扁钢来解决问题。
尺短寸长
发表于 2014-3-5 10:36:08
假如再考虑RCD故障时的人身安全,每个路灯设等电位联结就成为必然……
沿此思路深入下去,则大可不必采用TT系统,TN-S系统更有优势。
尺短寸长
发表于 2014-3-5 10:42:35
问题在于:
目前的市政道路、工厂道路、住宅小区道路旁的路灯,无论采用TN-S系统还是TT系统,有做等电位联结的吗?
请教老诚:
老诚做道路照明是咋做的?
治学以诚
发表于 2014-3-5 10:45:02
治学以诚
发表于 2014-3-5 10:47:28
治学以诚
发表于 2014-3-5 10:49:07
治学以诚
发表于 2014-3-5 10:53:22
治学以诚
发表于 2014-3-5 10:55:50
尺短寸长
发表于 2014-3-5 10:55:55
434.5.2 For cables and insulated conductors, all current caused by a short-circuit occurring
at any point of the circuit shall be interrupted in a time not exceeding that which brings the
insulation of the conductors to the permitted limit temperature.
For operating times of protective devices <0,1s where asymmetry of the current is of
importance and for current-limiting devices k2S2 shall be greater than the value of the letthrough
energy (I2t) quoted by the manufacturer of the protective device.
For short-circuits of duration up to 5s, the time t, in which a given short-circuit current will
raise the insulation of the conductors from the highest permissible temperature in normal duty
to the limit temperature can, as an approximation, be calculated from the formula:
t = (k * S / I)2 (3)
where
t is the duration, in s;
S is the cross-sectional area, in mm2;
I is the effective short-circuit current, in A, expressed as an r.m.s. value;
k is a factor taking account of the resistivity, temperature coefficient and heat capacity of
the conductor material, and the appropriate initial and final temperatures. For common
conductor insulation, the values of k for line conductors are shown in Table 43A.
老诚会说:你什么都不懂!
治学以诚
发表于 2014-3-5 10:57:32
rainmen_73
发表于 2014-3-5 10:57:36
回复 500# 尺短寸长
目前实际状况如不做市政设计的都不见得清楚,这个论坛上应该有。我想,可以从施工投资维护的角度来说说单灯做等电位联结的可行性。如此做法能推广,善莫大焉
治学以诚
发表于 2014-3-5 11:00:32
北方郎
发表于 2014-3-5 11:02:34
回复 497# 尺短寸长
看来能入老诚法眼的文章十分罕见{:4_118:}