发表于 2010-11-15 09:46:45
|
显示全部楼层
250.4 General Requirements for Grounding and Bond-
ing. 接地和搭接一般要求
A(5) Effective Ground-Fault Current Path. Electrical
equipment and wiring and other electrically conductive ma-
terial likely to become energized shall be installed in a
manner that creates a low-impedance circuit facilitating the
operation of the overcurrent device or ground detector for
high-impedance grounded systems. It shall be capable of
safely carrying the maximum ground-fault current likely to
be imposed on it from any point on the wiring system
where a ground fault may occur to the electrical supply
source. The earth shall not be considered as an effective
ground-fault current path.
排除了TT。
B(4) Path for Fault Current. Electrical equipment, wiring,
and other electrically conductive material likely to become
energized shall be installed in a manner that creates a low impedance circuit from any point on the wiring system to the electrical supply source to facilitate the operation of overcurrent devices should a second ground fault from a different phase occur on the wiring system. The earth shall not be considered as an effective fault-current path.
IT系统设备必须设有互联的PE。 |
评分
-
查看全部评分
|