702.55.101.3 Feed pumps, or other special electrical equipment especially intended for use in swimming pools located in a room or location adjacent to the swimming pool and accessible via a hatch (or door) located on the deck surrounding the swimming pool, shall be protected by one of the following protective measures:
a)SELV not exceeding 12 V a.c. or 30 V d.c. with the source being installed outside zones 0 and 1. Where the source of supply is installed in zone 2, 702.53 applies (see702.410.3.101.1);
b)electrical separation according to Clause 413 with simultaneous fulfilment of the following conditions:
– where the pump or other equipment is connected to the swimming pool basin, the connection shall only be made by non-conductive water piping;
– it shall only be possible to open the hatch or the door by means of a key or tool;
– all equipment installed in the room or location shall have a degree of protection of at least IPX5 or such protection shall be provided by an enclosure.
c)automatic disconnection of the power supply with simultaneous fulfilment of the following conditions:
– where the pump or other equipment is connected to the swimming pool basin, the connection shall be made by either electrically insulated water piping, or metal water piping connected to the pool basin's equipotential bonding:
– it shall only be possible to open the hatch or the door by means of a key or tool;
– all equipment installed in the room or location shall have a degree of protection of at least IPX5 or such protection shall be provided by an enclosure;
– additional equipotential bonding shall be installed in accordance with 702.415.2;
– the equipment shall be protected by a residual current protective device with a rated residual operating current not exceeding 30 mA.
NOTE The room where the equipment is located is considered to be outside zones 1 and 2. |
|