关于室外预埋电气管材的讨论
建筑电气与智能化通用规范7.2.8条要求埋在土壤里的接地导体应采用铜质材料或不锈钢材料,不应采用热浸锌钢材,是否因为热热浸锌容易腐蚀;而民标8.3.8条要求绝缘电线穿金属导管在室外埋地敷设时,应采用壁厚不小于2.0mm的热镀锌钢导管,并采取防水、防腐蚀措施。既然要防腐蚀,为什么还要采用热镀锌?欢迎讨论。data:image/png;base64,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:image/png;base64,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
7.2.8主要考虑的是电化学腐蚀,8.3.8是正常环境腐蚀 7.2.8讲的是当利用建筑物基础作为接地装置时,埋在土壤内的外接导体不能采用热浸锌钢材。是有前置条件的,不能就认为热浸锌刚才不能用。
页:
[1]