Brief Analysis of the Design of Automatic Fire Alarm System for Indoor Skiing Resort
ZHANG Xiao LI Liang FENG Xingming
(Central South Architectural Design Institute Co.,Ltd.,Wuhan 430071,China)
Abstract:Based on engineering practice,this paper analyzes the key and difficult points of electrical fire protection design for high and large spaces in an indoor skiing resort and introduces the design ideas and solutions for automatic fire alarm system design,alarm equipment selection and system configuration in an indoor skiing ground. It is suggested that the special performance‑based fire protection design undergo expert review as early as possible at the beginning of the project plan to clearly define the detection method and setup position of the automatic fire alarm system in advance and provide relevant solutions after a break from the conventional design.
Key words:indoor skiing resort;high and large space;electrical fire protection;key and difficult points of design;automatic fire alarm system;fire detector;manual fire alarm button;fire emergency broadcast
摘 要:结合工程实际,对室内滑雪场高大空间的电气消防设计重 / 难点进行分析,介绍室内滑雪场火灾自动报警系统设计、报警设备选择及系统配置的设计思路和解决方案,建议在项目方案初期尽早进行特殊消防性能化设计专家评审,提前明确火灾自动报警系统的探测方式、点位设置,以及突破常规设计后的相关解决方案。
关键词:室内滑雪场;高大空间;电气消防;设计重 / 难点;火灾自动报警系统;火灾探测器;手动火灾报警按钮;消防应急广播