Discussion on Quality Issues of Suspended Ceiling Electrical Installation Engineering
YU Yuelan(Architectural Design Institute,Huaqiao University(Quanzhou)
Co.,Ltd.,Quanzhou 362021,Fujian Province,China)
Abstract:After the secondary decoration of buildings,due to the use of a large amount of decoration materials and the increase of concealed processes,the fire risk of buildings increases significantly. During the on‑site inspection of the electrical installation of the suspended ceiling in the secondary decoration works,it was found that there were generally serious quality issues and potential electrical fire risks. This paper analyzes and discusses those issues according to relevant specifications based on common quality issues in the electrical installation of suspended ceilings on construction sites,and proposes improvement measures.
Key words:suspended ceiling;electrical;installation;quality;piping;trunk;wire connection;metal hose
摘 要: 建筑物二次装修后,由于大量装修材料的使用,以及隐蔽环节的增加,建筑物的火灾危险性也大幅度提高。现场查验二次装修工程的吊顶电气安装,发现普遍有比较严重的质量问题,存在电气火灾隐患。结合施工现场吊顶电气安装工程质量常见问题,根据相关规范进行分析探讨并提出改进措施。
关键词:吊顶;电气;安装;质量;配管;槽盒;导线连接;金属软管