某机房柴油发电机组动力不足的原因分析

来源于: 发表时间:2024-08-29 15:08 编辑:fzy

 

时庆兵(中国移动通信集团设计院有限公司安徽分公司,合肥市 230041

Analysis of Reason for Insufficient Power of Diesel Generator Unit

of a Certain Machine Room

SHI Qingbing(China Mobile Group Design Institute Co.,Ltd. Anhui Branch,Hefei 230041China)

 

 

AbstractBased on equipment condition and by means of site survey,the reserved area of air inlet / outlet of diesel generator room is calculated. Analysis shows that the reason for insufficient power of diesel generator unit is that the effective ventilation area of the shutters for noise reduction construction is insufficient. And relevant rectification measures are proposed.

Key wordsdiesel generator;machine room;power;air inlet area;air inlet volume;shutter;ventilation rate;mechanical ventilation

 

摘 要:通过现场勘察,结合设备情况,对柴油发电机房进出风口预留面积进行核算,分析柴油发电机组动力不足的原因是降噪施工中选用的百叶窗有效通风面积不足,并提出相应整改措施。

关键词:柴油发电机;机房;动力;进风口面积;进风量;百叶窗;通风率;机械通风