RCD应用若干问题探讨
刘叶语(中国航空规划设计研究总院有限公司,北京市 100120)
Discussion on Issued Related to RCD Application
LIU Yeyu(China Aviation Planning and Design Institute(Group)Co.,Ltd.,Beijing 100120,China)
Abstract:RCD is widely applied in the electric shock protection and fire protection,and the use scenarios and selection of RCD are involved in the design and construction drawing review. RCD is not a panacea with many limitations in actual application,
which shall not be used in greater scope of application. Combined with several application examples,the RCD action time,the role of RCD in fault protection to improve protection sensitivity,and the reflections on RCD application in facilities such as heating cables and electric heating film are discussed.
Key words:RCD;electric shock protection;fire protection;heating cables;buried heating systems;electrothermal film;electric heaters for air conditioning systems;break time
摘 要:RCD在电击防护、火灾防护方面的应用范围非常广泛,设计及施工图审查过程中,涉及到很多RCD的使用场合、选型要求等问题,RCD并不是万能的,在应用方面存在局限性,应避免使用范围扩大化。结合几个实例,阐述关于RCD动作时间、故障防护中RCD对提高保护灵敏度的作用,以及RCD在加热电缆和电热膜等设施中的应用体会。
关键词:RCD;电击防护;火灾防护;加热电缆;埋入式加热系统;电热膜;空调系统电加热器;分断时间
中图分类号:TU852 文献标识码:A
doi:10.3969 / j. issn.1003 - 8493.2021.03.002