李 蔚 陈 车 蔡雄飞(中信建筑设计研究总院有限公司,武汉市 430014)
Analysis on Difficulties in Electrical Design of Wuhan Huoshenshan Hospital
LI Wei CHEN Che CAI Xiongfei
(CITIC General Institute of Architectural Design and Research Co.,Ltd.,Wuhan 430014,China)
Abstract:Based on the current national specifications and standards, this paper analyses the 10 types of key and difficult issues which are highly ⁃ targeted, highly ⁃ concerned and commonality ⁃ based as selected and summarized from more than 200 related questions raised by netizens throughout the country when the author was live streaming according to the design of the electrical and intelligent systems of Wuhan Huoshenshan Hospital,thus providing reference for the design and construction of the electrical and intelligent systems for similar “ hospitals for emergency respiratory infectious disease”.
Key words:power supply reliability;overall design plan;power distribution wiring method;medical IT system;ultraviolet disinfection lamp;differential pressure monitoring;network architecture;modular design
摘 要:以国家现行规范和标准为依据,围绕武汉火神山医院电气与智能化系统设计,从笔者在线直播时全国网友们提出的200余条相关问题中,挑选、归纳出“针对性强、关注度高、带共性”的10类重点及难点问题进行详细解析,可供类似的“呼吸类应急传染病医院”电气与智能化系统设计与施工参考借鉴。
关键词:供电可靠性;整体设计方案;配电接线方式;医疗IT系统;紫外线消毒灯;压差监测;网络架构;模块化设计
中图分类号:TU246 文献标识码:A
doi:10.3969 / j. issn.1003 - 8493.2020.04.001