Discussion about On-line SPD Safety Performance Detection and Monitoring of Low-voltage Lines*
Bao Bingsheng(Zhejiang Oriental Lightning Protection Engineering Co.,Ltd.,Hangzhou 310 0 17,China)
Zhang Xiaodong(Zhejiang University City College,Hangzhou 310 0 10,China)
Abstract With the popularization and perfection of surge protective device(SPD)protection,more and more on-line SPD have been developed,but sufficient importance has not been attached by owners in the safety performance problem of on-line SPD in low-voltage lines that have been installed for years. In this paper,the requirements in the related specifications about safety performance maintenance and detection of on-line SPD are listed;some problems existing in the practical on-line SPD detection process are discussed;a kind of on-line SPD real-time dynamic monitoring and management system is presented;and the configuration of the software and hardware as well as the functions of the system are introduced.
Key words Surge protective device( SPD) Safety performance Detection Monitoring Management
摘 要 随着电涌保护器(SPD)防护技术的普及,在线 SPD 数量越来越多,但安装多年的低压线路在线 SPD 的安全性能问题并未引起业主的足够重视。文章列举了在线 SPD 安全性能维护、检测的相关规范要求,探讨了实际在线 SPD 检测过程中存在的一些问题,提出一种在线 SPD 实时动态监测、管理系统,并对该系统的软、硬件构架及功能进行了介绍。
关键词 电涌保护器 (SPD) 安全性能 检测 监测 管理