413.3.6 The exposed-conductive-parts of the separated circuit shall not be connected either
to the protective conductor or exposed-conductive-parts of other circuits, or to earth.
6.5 Protection by electrical separation
Electrical separation is achieved where the following conditions are met:
– basic protection is provided by basic insulation between hazardous-live-parts and exposed-conductive-parts of the separated circuit; and
– fault protection is provided
• by simple separation of the separated circuit from other circuits and earth, and
• by a protective-equipotential-bonding interconnecting exposed-conductive-parts of the separated circuit where more than one item of equipment is connected to the separated circuit. This protective-equipotential-bonding system shall not be earthed.
Intentional connection of exposed-conductive-parts to a protective earthing conductor or to an earthing conductor is not permitted. |
|