不会的。
建筑电气杂志 >> 2014年第02期(总第195期)
消火栓泵远程控制分析来源于: 发表时间:2014-02-27 16:02 编辑:fzy
鞠永健(同济大学建筑设计研究院(集团)有限公司,上海市 200092) Analysis on Remote Control of Fire Hydrant Pump
JYU Yongjian(Tongji Architectural Design(Group)Co.,Ltd.,Shanghai 200092,China)
Abstract:Control circuit diagrams given in the current standard collective drawings are modified to solve the contradictions of line safety and line drop. In addition,precautions for utilization of the modified control circuit diagrams are also given. Modification of the current standard collective drawings is based on the analysis of reasons and problems of shared fire hydrant pump rooms of multiple buildings,on the analysis and calculations via incorporating engineering cases of line drop due to remote control of fire hydrant pumps of multiple buildings,and on the analysis of such issues of start / stop and signal feedback of fire fighting control room.
Key words:fire hydrant pump;safe voltage;line drop;load moment;local relay box;control circuit;remote control
摘 要:分析多幢建筑物合用消火栓泵房的原因和存在的问题,结合工程案例分析计算多幢建筑远程控制消火栓泵的线路压降和消防控制室启停、信号反馈等问题,对现有标准图集中的控制电路图进行修改以解决线路安全和线路压降的矛盾,并对修改后的控制电路图使用注意事项进行说明。
关键词:消火栓泵;安全电压;线路压降;负荷矩;现场继电器箱;控制电路;远程控制
中图分类号:TU892 文献标识码:A
|