回复:PE线截面一定要取相线的S/2吗?
<P>按规定其电导不得小于相线电导的1/2,且要满足热稳定的要求。在一般情况下,保护线的截面可按下列原则选取:</P>
<P>当电源相线的截面A<SUB>φ<SUP>≤16mm</SUP></SUB><SUP>2</SUP>时,保护线的截面A<SUB>PE<SUP>=</SUP></SUB>A<SUB>φ;</SUB></P>
<P>当电源相线的截面<SUP><SUB>16mm</SUB>2</SUP>≤A<SUB>φ</SUB>≤35mm<SUP>2</SUP>时,A<SUB>PE</SUB>应取<SUP><SUB>16mm</SUB>2</SUP>;</P>
<P>当电源相线的截面Aφ≥35mm<SUP>2</SUP>时,A<SUB>PE<SUP>=</SUP></SUB>A<SUB>φ</SUB>/2。</P>
<P>当PE线采用单芯绝缘线时,GB50054-1995规定按机械强度要求,</P>
<P>有机械性保护时其截面A<SUB>PE</SUB>≥2.5<SUP><SUB>mm</SUB>2</SUP>;无机械性保护时,</P>
<P>其截面A<SUB>PE</SUB>≥4mm<SUP>2</SUP></P> |
|