账号:
密码:
建筑电气
 找回密码
 我要注册
楼主: 梁健

[求助] TN-C-S中的一句话

 火.. [复制链接]
发表于 2013-6-9 08:41:41 | 显示全部楼层
提示: 作者被禁止或删除 内容自动屏蔽
发表于 2013-6-9 15:29:51 | 显示全部楼层
对于这个问题,尺总分析的比较透切了。
     
发表于 2013-6-9 16:04:57 | 显示全部楼层
扩展到相距100米以外的A、B两建筑,远不是伸臂范围的问题了。A采用TT,接地后不立即切除,无论B采用TN-C还是TN-S,PEN、N、PE导线都会把中性点对大地零点电位带入到B建筑室内来。如果检修不断N线,不断PEN线(做总等与重复接地,仍然不可以消除与大地电位零点之间的电压),检修就存在电击风险。
治学以诚 发表于 2013-6-8 07:20


411.4.1 In TN systems the integrity of the earthing of the installation depends on the reliable and effective connection of the PEN or PE conductors to earth. Where the earthing is provided from a public or other supply system, compliance with the necessary conditions external to the installation is the responsibility of the supply network operator.

411.4.3 In fixed installations, a single conductor may serve both as a protective conductor and as a neutral conductor (PEN conductor) provided that the requirements of 543.4 of IEC 60364-5-54 are satisfied. No switching or isolating device shall be inserted in the PEN conductor.
发表于 2013-6-9 16:26:02 | 显示全部楼层
提示: 作者被禁止或删除 内容自动屏蔽
     
发表于 2013-6-9 16:46:58 | 显示全部楼层
NOTE 1 Examples of conditions include:
− the PEN is connected to earth at a number of points and is installed in such a way as to minimize the risk of a
break in the PEN conductor;
− RB/RE ≤ 50/(U0 – 50)
where
RB is the earth electrode resistance, in ohms, of all earth electrodes in parallel;
RE is the minimum contact resistance with earth, in ohms, of extraneous-conductive-parts not connected to a
protective conductor, through which a fault between line and earth may occur;
Uo is the nominal a.c. r.m.s. voltage to earth, in volts.
NOTE 2 In Germany compliance with condition RB/RE ≤ 50 / (Uo – 50) is compulsory for the supply network
operator.
     
发表于 2013-6-9 16:49:25 | 显示全部楼层
NOTE 1 Examples of conditions include:
− the PEN is connected to earth at a number of points and is installed in such a way as to minimize the risk of a break in the PEN conductor;
− RB/RE ≤ 50/(U0 – 50)
where
RB is the earth electrode resistance, in ohms, of all earth electrodes in parallel;
RE is the minimum contact resistance with earth, in ohms, of extraneous-conductive-parts not connected to a protective conductor, through which a fault between line and earth may occur;
Uo is the nominal a.c. r.m.s. voltage to earth, in volts.

NOTE 2 In Germany compliance with condition RB/RE ≤ 50 / (Uo – 50) is compulsory for the supply network operator.
发表于 2013-6-9 16:59:21 | 显示全部楼层
提示: 作者被禁止或删除 内容自动屏蔽
     
发表于 2013-6-9 17:03:05 | 显示全部楼层
狗屁,你给个电路,证明一下,PEN,重复接地与不重复接地,两者之间的危险性不就完了吗
治学以诚 发表于 2013-6-9 16:59


“IEC_60364-4-41:2005”=老诚破口大骂的 狗屁
发表于 2013-6-9 17:03:47 | 显示全部楼层
提示: 作者被禁止或删除 内容自动屏蔽
     
发表于 2013-6-9 17:05:30 | 显示全部楼层
老诚自己画的图,早已经证明了的。{:1_274:}
发表于 2013-6-9 17:06:30 | 显示全部楼层
提示: 作者被禁止或删除 内容自动屏蔽
     
发表于 2013-6-9 17:08:42 | 显示全部楼层
德国供电公司是“狗屁”?
发表于 2013-6-9 17:13:07 | 显示全部楼层
提示: 作者被禁止或删除 内容自动屏蔽
发表于 2013-6-9 17:16:04 | 显示全部楼层
提示: 作者被禁止或删除 内容自动屏蔽
     
发表于 2013-6-9 17:17:52 | 显示全部楼层
……
如TT系统,N线接地了,就不能再允许相线接地了。
治学以诚 发表于 2013-6-9 17:13


如TT系统,N线接地了,就不能再允许相线接地了。

好的。
那么,如TN系统,N线接地了,就允许相线接地了?
您需要登录后才可以回帖 登录 | 我要注册

本版积分规则