 楼主| 发表于 2008-2-29 15:58:45 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">12 低压配电线路其中电流最大一台电动机容量为55kW,电流<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="104" UnitName="a">104A</st1:chmetcnv>,起动倍数为6。 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">(1) 选择线路保护断路器为CW1型则其框架额定电流及断路器额定电流应为 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">A. <st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="200" UnitName="a">200A</st1:chmetcnv>,<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="160" UnitName="a">160A</st1:chmetcnv>   B. <st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="180" UnitName="a">180A</st1:chmetcnv>,<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="160" UnitName="a">160A</st1:chmetcnv>   C. <st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="160" UnitName="a">160A</st1:chmetcnv>,<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="160" UnitName="a">160A</st1:chmetcnv>   D. <st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="200" UnitName="a">200A</st1:chmetcnv>,<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="144" UnitName="a">144A</st1:chmetcnv> </P>
<P style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 17.95pt; mso-pagination: none; mso-char-indent-count: 1.71">根据&lt;&lt;通用用电设备配电设计规范(GB 50055-93)&gt;&gt; 第2.4.4条 “当交流电动机正常运行、正常起动或自起动时,短路保护器件不应误动作。为此,应符合下列规定:<o:p></o:p></P>
<P style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 17.95pt; mso-pagination: none; mso-char-indent-count: 1.71">三、瞬动过电流脱扣器或过电流继电器瞬动元件的整定电流,应取电动机起动电流的2~2.5倍。”的规定,依据&lt;&lt;工业与民用配电设计手册(第三版)&gt;&gt;668页的计算公式Iset&gt;114.4A</P>
<P style="TEXT-JUSTIFY: inter-ideograph; MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: justify; mso-pagination: none; tab-stops: 247.0pt"></P>
     
 楼主| 发表于 2008-2-29 16:05:11 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">13 住宅楼做总等电位联结,供电380/220V,TN-S系统,总箱到每户配电箱采用BV-3×<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="10" UnitName="mm">10mm</st1:chmetcnv><SUP>2</SUP>线,长度<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="15" UnitName="米">15米</st1:chmetcnv>。每户配电箱配出线BV-3×<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="2.5" UnitName="mm">2.5mm</st1:chmetcnv><SUP>2</SUP>。卫生间设有插座,插座接用电设备线3×<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="2.5" UnitName="mm">2.5mm</st1:chmetcnv><SUP>2</SUP>,长<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="2" UnitName="米">2米</st1:chmetcnv>。卫生间做局部等电位联结。卫生间至每户配电箱电线长度<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="5" UnitName="米">5米</st1:chmetcnv>。 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">(1)由每户配电箱PE线,接线BV<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="True" HasSpace="False" SourceValue="2.5" UnitName="mm">-2.5mm</st1:chmetcnv><SUP>2</SUP>至卫生间LEB,作为PE线与卫生间LEB之间的等电位联结。当卫生间插座所接用电设备内的相线碰金属外壳时,该用电设备的金属外壳与卫生间地之间的电压是多少? (图片粘贴不上,抱歉了)</P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">答:2.5mm<SUP>2</SUP>导体的相线与保护线回路每米的电阻为R<SUB>0</SUB>(忽略线路电抗),则<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="10" UnitName="mm">10mm</st1:chmetcnv><SUP>2</SUP>导体的相线与保护线回路每米的电阻为0.25R,忽略AP1配电箱与AP2配电箱及主等电位联结接地与电源系统中性点接地并联阻抗,接地故障电流Id=U0/10.75R0(V),其接触电压Uc=71.6V.</P>
     
 楼主| 发表于 2008-2-29 16:06:18 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">(2)由卫生间插座PE线,接线<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="2" UnitName="米">2米</st1:chmetcnv>BV<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="True" HasSpace="False" SourceValue="2.5" UnitName="mm">-2.5mm</st1:chmetcnv><SUP>2</SUP>至卫生间LEB,作为PE线与卫生间LEB之间的等电位联结。当卫生间插座所接用电设备内的相线碰金属外壳时,该用电设备的金属外壳与卫生间地之间的电压是多少?</P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">答案:Uc=20.5V</P>
     
 楼主| 发表于 2008-2-29 16:07:07 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">14.某110kV变电所,采用图2所示的方孔接地网,其占地面积为<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="60" UnitName="m">60m</st1:chmetcnv>×<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="60" UnitName="m">60m</st1:chmetcnv>,材料为<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="40" UnitName="mm">40mm</st1:chmetcnv>×<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="4" UnitName="mm">4mm</st1:chmetcnv>扁纲,埋入深度为<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue=".8" UnitName="m">0.8m</st1:chmetcnv>,其接地电阻R=0.1Ω,计算用入地短路电流为20kA,那么该变电所接地网外的地表面最大跨步电压最接近的数值是: <BR>A 140V     B 160V     C 200V     D 300V。 <o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center><v:shapetype id=_x0000_t75 stroked="f" filled="f" path="m@4@5l@4@11@9@11@9@5xe" o:preferrelative="t" o:spt="75" coordsize="21600,21600"><v:stroke joinstyle="miter"></v:stroke><v:formulas><v:f eqn="if lineDrawn pixelLineWidth 0"></v:f><v:f eqn="sum @0 1 0"></v:f><v:f eqn="sum 0 0 @1"></v:f><v:f eqn="prod @2 1 2"></v:f><v:f eqn="prod @3 21600 pixelWidth"></v:f><v:f eqn="prod @3 21600 pixelHeight"></v:f><v:f eqn="sum @0 0 1"></v:f><v:f eqn="prod @6 1 2"></v:f><v:f eqn="prod @7 21600 pixelWidth"></v:f><v:f eqn="sum @8 21600 0"></v:f><v:f eqn="prod @7 21600 pixelHeight"></v:f><v:f eqn="sum @10 21600 0"></v:f></v:formulas><v:path o:connecttype="rect" gradientshapeok="t" o:extrusionok="f"></v:path><o:lock aspectratio="t" v:ext="edit"></o:lock></v:shapetype><v:shape id=_x0000_i1025 style="WIDTH: 89.25pt; HEIGHT: 89.25pt" type="#_x0000_t75"><v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image001.emz"></v:imagedata></v:shape><o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>图2 方空接地网<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>(等距圆角方格,n=4)<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">计算方法见《交流电气装置的接地》DL/T621-1997附录B发电厂、变电所经接地装置的入地短路电流及电位计算<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">B2  发生接地故障时,接地装置的电位、接触电位差和跨步电位差的计算<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">    2)接地网外的地表面最大跨步电位差可按下式计算<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center><I style="mso-bidi-font-style: normal">U</I><SUB>smax</SUB> = <I style="mso-bidi-font-style: normal">K</I><SUB>smax</SUB><I style="mso-bidi-font-style: normal">U</I><SUB>g</SUB><o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">式中:<I style="mso-bidi-font-style: normal">U</I><SUB>smax</SUB>——最大跨步电位差,<I style="mso-bidi-font-style: normal">V</I>;<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">       <I style="mso-bidi-font-style: normal">K</I><SUB>smax</SUB>——最大跨步电位差系数。<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">    正方形接地网的最大跨步电位差系数可按下式计算<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; WORD-BREAK: break-all; TEXT-ALIGN: right" align=right><v:shape id=_x0000_i1032 style="WIDTH: 227.25pt; HEIGHT: 54pt" type="#_x0000_t75" o:ole=""><v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image003.wmz"></v:imagedata></v:shape>                      <o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center><v:shape id=_x0000_i1026 style="WIDTH: 111pt; HEIGHT: 28.5pt" type="#_x0000_t75" o:ole=""><v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image005.wmz"></v:imagedata></v:shape><o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center><SUB><v:shape id=_x0000_i1027 style="WIDTH: 51.75pt; HEIGHT: 18.75pt" type="#_x0000_t75"><v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image007.wmz"></v:imagedata></v:shape><o:p></o:p></SUB></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">      <I style="mso-bidi-font-style: normal">S</I>——接地网的总面积,m<SUP>2</SUP>;<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">      <I style="mso-bidi-font-style: normal">d</I>——水平接地极的直径或等效直径,m;<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><o:p> </o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">       接地极用圆钢时,圆钢的直径,m[当用其他型式钢材时,其等效直径应按下式计算(图A2):钢管,<I style="mso-bidi-font-style: normal">d</I>=<I style="mso-bidi-font-style: normal">d</I><SUB>1</SUB>;扁钢,<v:shape id=_x0000_i1033 style="WIDTH: 38.25pt; HEIGHT: 32.25pt" type="#_x0000_t75" o:ole=""> <v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image009.wmz"></v:imagedata></v:shape>;等边角钢,<I style="mso-bidi-font-style: normal">d</I>=0.84<I style="mso-bidi-font-style: normal">b</I>;不等边角钢,<v:shape id=_x0000_i1034 style="WIDTH: 131.25pt; HEIGHT: 23.25pt" type="#_x0000_t75" o:ole=""> <v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image011.wmz"></v:imagedata></v:shape>]。<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; TEXT-ALIGN: center; mso-layout-grid-align: none" align=center><v:shape id=_x0000_i1035 style="WIDTH: 24pt; HEIGHT: 24pt" alt="" type="#_x0000_t75"></v:shape><v:shape id=_x0000_i1036 style="WIDTH: 210pt; HEIGHT: 163.5pt" type="#_x0000_t75"><v:imagedata o:title="imagee-038" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image014.png"></v:imagedata></v:shape><o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; TEXT-ALIGN: center; mso-layout-grid-align: none" align=center>图A2  几种型式钢材的计算用尺寸<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; TEXT-ALIGN: center; mso-layout-grid-align: none" align=center><o:p> </o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">      <I style="mso-bidi-font-style: normal">h</I>——水平接地极的埋设深度,m;<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">      <I style="mso-bidi-font-style: normal">L</I><SUB>0</SUB>——接地网的外缘边线总长度,m;<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">      <I style="mso-bidi-font-style: normal">L</I>——水平接地极的总长度,m。<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">    对于矩形接地网,<I style="mso-bidi-font-style: normal">n</I>值由下式计算<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; TEXT-ALIGN: center; mso-layout-grid-align: none" align=center><v:shape id=_x0000_i1028 style="WIDTH: 96.75pt; HEIGHT: 35.25pt" type="#_x0000_t75" o:ole=""><v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image016.wmz"></v:imagedata></v:shape><o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><o:p> </o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">T=<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue=".8" UnitName="m">0.8m</st1:chmetcnv>,即跨步距离。<v:shape id=_x0000_i1037 style="WIDTH: 9.75pt; HEIGHT: 17.25pt" type="#_x0000_t75" o:ole=""> <v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image018.wmz"></v:imagedata></v:shape><o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><v:shape id=_x0000_i1029 style="WIDTH: 149.25pt; HEIGHT: 20.25pt" type="#_x0000_t75" o:ole=""><v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image020.wmz"></v:imagedata></v:shape><B><o:p></o:p></B></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><v:shape id=_x0000_i1038 style="WIDTH: 416.25pt; HEIGHT: 33.75pt" type="#_x0000_t75" o:ole=""><v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image022.wmz"></v:imagedata></v:shape><v:shape id=_x0000_i1030 style="WIDTH: 330pt; HEIGHT: 105.75pt" type="#_x0000_t75" o:ole=""><v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image024.wmz"></v:imagedata></v:shape><B><o:p></o:p></B></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><B><o:p> </o:p></B></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><B><v:shape id=_x0000_i1031 style="WIDTH: 227.25pt; HEIGHT: 21pt" type="#_x0000_t75" o:ole=""><v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image026.wmz"></v:imagedata></v:shape>V<o:p></o:p></B></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><B><o:p> </o:p></B></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">参考答案:B<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><B><o:p> </o:p></B></P>
     
 楼主| 发表于 2008-2-29 16:08:55 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

中间一些图形即使用CAD画了也没法粘贴出来,大家凑和着看看,当学习用了!
     
 楼主| 发表于 2008-2-29 16:12:59 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">15 10kV处,某用户5次谐波电流<st1:chmetcnv w:st="on" TCSC="0" NumberType="1" Negative="False" HasSpace="False" SourceValue="17" UnitName="a">17A</st1:chmetcnv>,已知短路容量200MVA,求5次谐波电压含有率 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><o:p> </o:p></P>
<P style="MARGIN: 0cm 0cm 0pt; mso-pagination: none">根据&lt;电能质量 公用电网谐波(GB/T 14549-1993)&gt;附录C谐波的基本计算式(补充件)C1  第h次谐波电压含有率HRU<SUB>h</SUB>与第h次谐波电流分量I<SUB>h</SUB>的关系:</P>
<P style="MARGIN: 0cm 0cm 0pt; mso-pagination: none">HRUh=1.732Un*h*Ih/10*Sk(%)                (C2)<o:p></o:p></P>
<P style="TEXT-JUSTIFY: inter-ideograph; MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: justify; mso-pagination: none">式中  U<SUB>N</SUB>-电网的标称电压,kV;<o:p></o:p></P>
<P style="TEXT-JUSTIFY: inter-ideograph; MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: justify; mso-pagination: none">      S<SUB>k</SUB>-公共连接点的三相短路容量,MVA;<o:p></o:p></P>
<P style="TEXT-JUSTIFY: inter-ideograph; MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: justify; mso-pagination: none">      I<SUB>h</SUB>-第h次谐波电流,A;</P>
<P style="TEXT-JUSTIFY: inter-ideograph; MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: justify; mso-pagination: none">可算出HRUh=0.74%</P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><B><o:p> </o:p></B></P><v:shape id=_x0000_i1026 style="WIDTH: 312pt; HEIGHT: 38.25pt" type="#_x0000_t75" o:ole=""><v:imagedata o:title="" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image003.wmz"></v:imagedata></v:shape>
     
 楼主| 发表于 2008-2-29 16:15:06 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">16.某10kV六相整流器,5次谐波电流17,求7次谐波电流<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><B><o:p> </o:p></B></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 21pt; mso-char-indent-count: 2.0">根据&lt;&lt;工业与民用配电设计手册(第三版)&gt;&gt;第282页常用整流器负荷电流的谐波次数、谐波电流及含量(理论最大值)见表(6-20)。<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 21pt; mso-char-indent-count: 2.0"><o:p> </o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">表(6-20)  常用整流器负荷电流的谐波次数、谐波电流及含量(理论最大值)单位:%<o:p></o:p></P>
<TABLE class=MsoNormalTable style="BORDER-RIGHT: medium none; BORDER-TOP: medium none; BORDER-LEFT: medium none; WIDTH: 437.6pt; BORDER-BOTTOM: medium none; BORDER-COLLAPSE: collapse; mso-padding-alt: 0cm 5.4pt 0cm 5.4pt; mso-border-top-alt: solid black 1.5pt; mso-border-bottom-alt: solid black 1.5pt; mso-yfti-tbllook: 191; mso-border-insideh: cell-none; mso-border-insidev: cell-none" cellSpacing=0 cellPadding=0 width=583 border=1>

<TR style="HEIGHT: 15.55pt; mso-yfti-irow: 0; mso-yfti-firstrow: yes; page-break-inside: avoid">
<TD style="BORDER-RIGHT: black 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: windowtext 1pt solid; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 49.3pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-top-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid black .75pt" vAlign=top width=66 rowSpan=2>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">整流电路接线方式<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: windowtext 1pt solid; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 52.8pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-alt: solid windowtext .5pt; mso-border-left-alt: solid black .75pt" vAlign=top width=70 rowSpan=2>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">整流电路相数<I>p</I><o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: windowtext 1pt solid; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 245.3pt; PADDING-TOP: 0cm; BORDER-BOTTOM: black 1pt solid; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-alt: solid windowtext .5pt; mso-border-left-alt: solid windowtext .5pt; mso-border-bottom-alt: solid black .75pt" vAlign=top width=327 colSpan=9>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center><B><I>I<SUB>n</SUB>/I<SUB>1</SUB></I></B><o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: windowtext 1pt solid; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 45pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-alt: solid windowtext .5pt; mso-border-left-alt: solid windowtext .5pt" vAlign=top width=60 rowSpan=2>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt"><v:shapetype id=_x0000_t75 stroked="f" filled="f" path="m@4@5l@4@11@9@11@9@5xe" o:preferrelative="t" o:spt="75" coordsize="21600,21600"><v:stroke joinstyle="miter"></v:stroke><v:formulas><v:f eqn="if lineDrawn pixelLineWidth 0"></v:f><v:f eqn="sum @0 1 0"></v:f><v:f eqn="sum 0 0 @1"></v:f><v:f eqn="prod @2 1 2"></v:f><v:f eqn="prod @3 21600 pixelWidth"></v:f><v:f eqn="prod @3 21600 pixelHeight"></v:f><v:f eqn="sum @0 0 1"></v:f><v:f eqn="prod @6 1 2"></v:f><v:f eqn="prod @7 21600 pixelWidth"></v:f><v:f eqn="sum @8 21600 0"></v:f><v:f eqn="prod @7 21600 pixelHeight"></v:f><v:f eqn="sum @10 21600 0"></v:f></v:formulas><v:path o:connecttype="rect" gradientshapeok="t" o:extrusionok="f"></v:path><o:lock aspectratio="t" v:ext="edit"></o:lock></v:shapetype><v:shape id=_x0000_s1027 style="MARGIN-TOP: 7.3pt; Z-INDEX: -5; LEFT: 0px; MARGIN-LEFT: -5.4pt; WIDTH: 36.5pt; POSITION: absolute; HEIGHT: 15.75pt; TEXT-ALIGN: left; mso-wrap-edited: f; mso-position-horizontal-relative: text; mso-position-vertical-relative: text" type="#_x0000_t75" wrapcoords="-86 0 -86 21465 21600 21465 21600 0 -86 0"><v:imagedata o:title="A4" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image001.wmz"></v:imagedata></v:shape><v:shape id=_x0000_s1029 style="MARGIN-TOP: 23.15pt; Z-INDEX: -3; LEFT: 0px; MARGIN-LEFT: 11.15pt; WIDTH: 12.4pt; POSITION: absolute; HEIGHT: 7.9pt; TEXT-ALIGN: left; mso-wrap-edited: f; mso-position-horizontal-relative: text; mso-position-vertical-relative: text" type="#_x0000_t75" wrapcoords="-164 0 -164 21343 21600 21343 21600 0 -164 0"><v:imagedata o:title="A7" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image003.wmz"></v:imagedata></v:shape><o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: #d4d0c8; PADDING-RIGHT: 5.4pt; BORDER-TOP: windowtext 1pt solid; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 45.2pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt" vAlign=top width=60 rowSpan=2>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt"><v:shape id=_x0000_s1028 style="MARGIN-TOP: 7.3pt; Z-INDEX: -4; LEFT: 0px; MARGIN-LEFT: -5.4pt; WIDTH: 36.2pt; POSITION: absolute; HEIGHT: 15.8pt; TEXT-ALIGN: left; mso-wrap-edited: f; mso-position-horizontal-relative: text; mso-position-vertical-relative: text" type="#_x0000_t75" wrapcoords="-38 0 -38 21540 21600 21540 21600 0 -38 0"><v:imagedata o:title="A5" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image005.wmz"></v:imagedata></v:shape><v:shape id=_x0000_s1030 style="MARGIN-TOP: 23.15pt; Z-INDEX: -2; LEFT: 0px; MARGIN-LEFT: 7pt; WIDTH: 12.9pt; POSITION: absolute; HEIGHT: 8.2pt; TEXT-ALIGN: left; mso-wrap-edited: f; mso-position-horizontal-relative: text; mso-position-vertical-relative: text" type="#_x0000_t75" wrapcoords="-164 0 -164 21343 21600 21343 21600 0 -164 0"><v:imagedata o:title="A8" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image007.wmz"></v:imagedata></v:shape><o:p></o:p></P></TD></TR>
<TR style="HEIGHT: 7pt; mso-yfti-irow: 1; page-break-inside: avoid">
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-alt: solid windowtext .5pt; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid black .75pt" vAlign=top width=36>
<P class=MsoHeader style="BORDER-RIGHT: medium none; BORDER-TOP: medium none; MARGIN: 0cm 0cm 0pt; BORDER-LEFT: medium none; LAYOUT-GRID-MODE: both; BORDER-BOTTOM: medium none; tab-stops: 21.0pt; mso-padding-alt: 0cm 0cm 0cm 0cm">n=1<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 26.8pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-alt: solid windowtext .5pt; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid black .75pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>5<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 26.8pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-alt: solid windowtext .5pt; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid black .75pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>7<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-alt: solid windowtext .5pt; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid black .75pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>11<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-alt: solid windowtext .5pt; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid black .75pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>13<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-alt: solid windowtext .5pt; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid black .75pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>17<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-alt: solid windowtext .5pt; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid black .75pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>19<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-alt: solid windowtext .5pt; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid black .75pt" vAlign=top width=36>
<P class=MsoHeader style="BORDER-RIGHT: medium none; BORDER-TOP: medium none; MARGIN: 0cm 0cm 0pt; BORDER-LEFT: medium none; LAYOUT-GRID-MODE: both; BORDER-BOTTOM: medium none; tab-stops: 21.0pt; mso-padding-alt: 0cm 0cm 0cm 0cm">23<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 29.7pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-alt: solid windowtext .5pt; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid black .75pt" vAlign=top width=40>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>25<o:p></o:p></P></TD></TR>
<TR style="HEIGHT: 15.55pt; mso-yfti-irow: 2; page-break-inside: avoid">
<TD style="BORDER-RIGHT: black 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 49.3pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-top-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid black .75pt" vAlign=top width=66 rowSpan=2>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">三相桥式整流<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 52.8pt; PADDING-TOP: 0cm; BORDER-BOTTOM: #d4d0c8; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid black .75pt; mso-border-top-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=70>
<P class=MsoHeader style="BORDER-RIGHT: medium none; BORDER-TOP: medium none; MARGIN: 0cm 0cm 0pt; BORDER-LEFT: medium none; LAYOUT-GRID-MODE: both; BORDER-BOTTOM: medium none; tab-stops: 21.0pt; mso-padding-alt: 0cm 0cm 0cm 0cm">6<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: #d4d0c8; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>100<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 26.8pt; PADDING-TOP: 0cm; BORDER-BOTTOM: #d4d0c8; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>20<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 26.8pt; PADDING-TOP: 0cm; BORDER-BOTTOM: #d4d0c8; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>14<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: #d4d0c8; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>9.1<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: #d4d0c8; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>7.7<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: #d4d0c8; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>5.9<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: #d4d0c8; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>5.3<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: #d4d0c8; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>4.3<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 29.7pt; PADDING-TOP: 0cm; BORDER-BOTTOM: #d4d0c8; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=40>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>4<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 45pt; PADDING-TOP: 0cm; BORDER-BOTTOM: #d4d0c8; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=60>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>28.9<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: #d4d0c8; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 45.2pt; PADDING-TOP: 0cm; BORDER-BOTTOM: #d4d0c8; HEIGHT: 15.55pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-top-alt: solid windowtext .5pt" vAlign=top width=60>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>104.1<o:p></o:p></P></TD></TR>
<TR style="HEIGHT: 7pt; mso-yfti-irow: 3; mso-yfti-lastrow: yes; page-break-inside: avoid">
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 52.8pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid black .75pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=70>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>12<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>100<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 26.8pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>0<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 26.8pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>0<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>9.1<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>7.7<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>0<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>0<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 27pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=36>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>4.3<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 29.7pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=40>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>4<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: windowtext 1pt solid; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 45pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt; mso-border-right-alt: solid windowtext .5pt" vAlign=top width=60>
<P class=MsoHeader style="BORDER-RIGHT: medium none; BORDER-TOP: medium none; MARGIN: 0cm 0cm 0pt; BORDER-LEFT: medium none; LAYOUT-GRID-MODE: both; BORDER-BOTTOM: medium none; tab-stops: 21.0pt; mso-padding-alt: 0cm 0cm 0cm 0cm">13.3<o:p></o:p></P></TD>
<TD style="BORDER-RIGHT: #d4d0c8; PADDING-RIGHT: 5.4pt; BORDER-TOP: #d4d0c8; PADDING-LEFT: 5.4pt; PADDING-BOTTOM: 0cm; BORDER-LEFT: #d4d0c8; WIDTH: 45.2pt; PADDING-TOP: 0cm; BORDER-BOTTOM: windowtext 1pt solid; HEIGHT: 7pt; BACKGROUND-COLOR: transparent; mso-border-left-alt: solid windowtext .5pt; mso-border-bottom-alt: solid windowtext .5pt" vAlign=top width=60>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-ALIGN: center" align=center>100.9<o:p></o:p></P></TD></TR></TABLE>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt"><v:shape id=_x0000_s1031 style="MARGIN-TOP: 5.55pt; Z-INDEX: -1; LEFT: 0px; MARGIN-LEFT: 117pt; WIDTH: 27pt; POSITION: absolute; HEIGHT: 15.6pt; TEXT-ALIGN: left; mso-wrap-edited: f; mso-position-horizontal-relative: text; mso-position-vertical-relative: text" type="#_x0000_t75" wrapcoords="-38 0 -38 21540 21600 21540 21600 0 -38 0"><v:imagedata o:title="A7" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image009.wmz"><FONT size=3></FONT></v:imagedata></v:shape>①六相及十二相时的谐波含量      分别为29.9%和14.2%。<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt"><v:shape id=_x0000_s1026 style="MARGIN-TOP: 5.55pt; Z-INDEX: -6; LEFT: 0px; MARGIN-LEFT: 117pt; WIDTH: 27pt; POSITION: absolute; HEIGHT: 15.6pt; TEXT-ALIGN: left; mso-wrap-edited: f" type="#_x0000_t75" wrapcoords="-38 0 -38 21540 21600 21540 21600 0 -38 0"><v:imagedata o:title="A6" src="file:///C:\DOCUME~1\ADMINI~1\LOCALS~1\Temp\msohtml1\01\clip_image011.wmz"></v:imagedata></v:shape>②六相及十二相时的负荷电流      分别为104.4%和101.0%。<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><B><o:p> </o:p></B></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">基波电流方均根值I1=I5*N=75A<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">7次谐波电流方均根值I7=I1/7=12.1A<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><o:p> </o:p></P>
     
 楼主| 发表于 2008-2-29 16:17:09 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

发到这里,我们可以得出第一个结论: <STRONG>&lt;&lt;工业与民用配电设计手册(第三版)&gt;&gt;很重要!!!大家要好好学习!</STRONG>
     
 楼主| 发表于 2008-2-29 16:19:36 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

<P>我认为:只要把<STRONG>&lt;&lt;工业与民用配电设计手册(第三版)&gt;&gt;学习完,通过第二天专业案例考试基本没有问题的!!!至于第一天的考试,大家对各种电气有关设计规范熟悉即可,通过也是问题不大的!这就是我的经验。</STRONG></P>
     
 楼主| 发表于 2008-3-3 09:34:18 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">17.220/380V供电系统,室外金属栏栅处发生单相接地,变压器中性点接地电阻R<SUB>b</SUB>=4Ω,金属栏栅接地电阻R<SUB>d</SUB>=10Ω,问 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">1)接地故障电流 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">2)建筑物内用电设备金属外壳的接触电压 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">3)户外用电设备金属外壳的接触电压 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">4)如果要将户外用电设备金属外壳的接触电压降低到50V以下,R<SUB>b</SUB>应不大于多少欧姆 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">此题涉及到图形及公式,留待大家解答</P>
     
 楼主| 发表于 2008-3-3 09:34:56 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">18.室内变电所的变压器,油量为多少及以上时,应设置单独的变压器室: </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">A  60    B  <st1:chmetcnv UnitName="C" SourceValue="80" HasSpace="True" Negative="False" NumberType="1" TCSC="0" w:st="on">80    C</st1:chmetcnv>  100    D   120</P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt"> </P>
<P style="MARGIN: 0cm 0cm 0pt; mso-pagination: none">&lt;10kV 及以下变电所设计规范(GB50053-94)&gt;第<st1:chsdate w:st="on" IsROCDate="False" IsLunarDate="False" Day="30" Month="12" Year="1899">4.1.4</st1:chsdate>条 室内变电所的每台油量为<st1:chmetcnv UnitName="kg" SourceValue="100" HasSpace="False" Negative="False" NumberType="1" TCSC="0" w:st="on">100kg</st1:chmetcnv>及以上的三相变压器,应设在单独的变压器室内。<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt"><o:p> </o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">参考答案:C<o:p></o:p></P>
     
 楼主| 发表于 2008-3-3 09:35:24 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">19. 正常运行情况下,用电设备端子处电压偏差允许值: </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">A、电动机为±5%;照明在一般工作场所为±5%;无特殊要求时为±5%。 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">B、电动机为±5%;照明在一般工作场所为+5%、-10%;无特殊要求时为±5%。 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">C、电动机为±5%;照明在一般工作场所为+5%、-10%;无特殊要求时为+5%、-10%。 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">D、电动机为±5%;照明在一般工作场所为±5%;无特殊要求时为+5%、-10%。 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt"><o:p> </o:p></P>
<P style="MARGIN: 0cm 0cm 0pt; mso-pagination: none">     &lt;供配电系统设计规范(GB50052-95)&gt;第<st1:chsdate w:st="on" IsROCDate="False" IsLunarDate="False" Day="30" Month="12" Year="1899">4.0.4</st1:chsdate>条正常运行情况下,用电设备端子处电压偏差允许值(以额定电压的百分数表示)宜符合下列要求:<o:p></o:p></P>
<P style="MARGIN: 0cm 0cm 0pt; mso-pagination: none">     一、电动机为±5%。<o:p></o:p></P>
<P style="MARGIN: 0cm 0cm 0pt; mso-pagination: none">     二、照明:在一般工作场所为±5%;对于远离变电所的小面积一般工作场所,难以满足上述要求时,可为+5%,-10%;应急照明、道路照明和警卫照明等为+5%、-10%。<o:p></o:p></P>
<P style="MARGIN: 0cm 0cm 0pt; mso-pagination: none">     三、其它用电设备当无特殊规定时为±5%。<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt"><o:p> </o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">参考答案:A </P>
     
 楼主| 发表于 2008-3-3 09:36:07 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">20.环境允许的中小城镇居民区,变压器容量在多少时,宜设杆上式或高台式变电所: </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">A  630    B  <st1:chmetcnv UnitName="C" SourceValue="500" HasSpace="True" Negative="False" NumberType="1" TCSC="0" w:st="on"><st1:chmetcnv UnitName="C" SourceValue="500" HasSpace="False" Negative="False" NumberType="1" TCSC="0" w:st="on">500 </st1:chmetcnv>  C</st1:chmetcnv>  200   D  315 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><o:p> </o:p></P>
<P style="MARGIN: 0cm 0cm 0pt; mso-pagination: none">&lt;民用电气设计规范(JGJ?T16-92)&gt;<st1:chsdate w:st="on" IsROCDate="False" IsLunarDate="False" Day="30" Month="12" Year="1899">4.5.1</st1:chsdate> 配变电所的形式应根据用电负荷的状况和周围环境情况综合确定。<o:p></o:p></P>
<P style="MARGIN: 0cm 0cm 0pt; mso-pagination: none">     <st1:chsdate w:st="on" IsROCDate="False" IsLunarDate="False" Day="30" Month="12" Year="1899">4.5.1</st1:chsdate>.1 高层或大型民用建筑内,宜设室内变电所或户内成套变电所。<o:p></o:p></P>
<P style="MARGIN: 0cm 0cm 0pt; mso-pagination: none">     <st1:chsdate w:st="on" IsROCDate="False" IsLunarDate="False" Day="30" Month="12" Year="1899">4.5.1</st1:chsdate>.2 大中城市的居民区,宜设独立变电所或内外附变电所,有条件时也可设户外成套变电所。<o:p></o:p></P>
<P style="MARGIN: 0cm 0cm 0pt; mso-pagination: none">     <st1:chsdate w:st="on" IsROCDate="False" IsLunarDate="False" Day="30" Month="12" Year="1899">4.5.1</st1:chsdate>.3 环境允许的中小城镇居民区和工厂的生活区,其变压器容量在315kV·A以下时,宜设杆上式和高台式变电所。<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><o:p> </o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">参考答案:D<o:p></o:p></P>
     
 楼主| 发表于 2008-3-3 09:36:23 | 显示全部楼层

回复:重磅推出:全国注册电气案例题真题披露及解答过程

<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">21. 低压配电宜用放射式配电的为: </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">A用电设备容量较大;                B用电负荷性质重要; </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt">C有特殊要求的车间、建筑物内;      D用电设备彼此靠近。 </P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><o:p> </o:p></P>
<P style="MARGIN: 0cm 0cm 0pt; mso-pagination: none"> &lt;供配电系统设计规范(GB50052-95)&gt;<FONT face="宋体, MS Song"> </FONT>第<st1:chsdate w:st="on" IsROCDate="False" IsLunarDate="False" Day="30" Month="12" Year="1899">6.0.3</st1:chsdate>条当用电设备为大容量,或负荷性质重要,或在有特殊要求的车间、建筑物内,宜采用放射式配电。<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none"><o:p> </o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; LAYOUT-GRID-MODE: char; mso-layout-grid-align: none">参考答案:ABC<o:p></o:p></P>