附一个完整的表吧
A Exit Route
"疏散路径"
V.A.1 Are all gaps, openings & penetrations are fully sealed and compartmented in exit route?
"是否疏散路径上所有缝隙、开口及穿透处需完全密封及隔离?"
V.A.2 If at least 1/2 people and 1/2 exit are discharged directly to exterior on level of discharge.
"是否在底层有至少1/2的人数和至少1/2的疏散出口直接对外?"
V.A.3 If exit route free from combustible material and unblocked?
"疏散路径是否无可燃物并保持畅通?"
V.A.4 If exit route well illuminated during normal power loss (By generator and EPS)?
"疏散路径在正常供电停止时是否可以有效照明 (有发电机照明及电池照明)?"
V.A.5 Is evacuation signal installed at high position of turnings?
"转角高位是否安装了疏散指示?"
V.A.6 Do stair wider than 1.2m have hand rail on both side?
"宽于1.2米的楼梯是否有两把扶手?"
V.A.7 Is smoke detector installed at the top of stairwell?
"楼梯顶部是否装有烟感?"
V.A.8 Are sprinklers installed at the top and below the bottom landing of stairwell?
"楼梯顶部及底部半平台下是否安装有喷淋?"
V.A.9 Are evacuation speakers installed at each 5 level in stairwell?
"是否楼梯间每5层安装有疏散喇叭?"
V.A.10 Is self closing and latching device functional along egress path and at exit staircase?
"疏散通道和楼梯间的自动关闭和斜舌装置是否良好?"
V.A.11 Are door selectors used for double fire doors functional along egress path and at exit staircase?
"疏散通道和楼梯间的双开门闭门选择器是否良好?"
V.A.12 If exit door is unlocked and easy to open during emergency?
"是否出口门不上锁并在紧急情况下能轻易打开?"
V.A.13 Are panic bars installed in exit door to outdoor?
"通室外的疏散门是否采用了推杆锁?"
V.A.14 Have access controlled door auto release function and break glass button installed?
"门禁锁是否有自动释放及破玻按钮?"
|
|