按编制者的说明,6.2.7条由IEC60364-4-43-2008 434.3条而来,先看看原文。
434.3 Omission of devices for protection against short-circuit
Provided that both of the following conditions are simultaneously fulfilled:
• the wiring is installed in such a way as to reduce the risk of a short-circuit to a
minimum (see item b) of 434.2.1), and
• the wiring is not placed close to combustible material,
devices for protection against short-circuit need not be provided for applications such as:
a) conductors connecting generators, transformers, rectifiers, accumulator batteries to the
associated control panels, the protective devices being placed in these panels;
b) circuits where disconnection could cause danger for the operation of the installations
concerned, such as those cited in 433.3.3;
c) certain measuring circuits;
d) at the origin of an installation where the distributor installs one or more devices providing
protection against short-circuit and agrees that such a device affords protection to the part
of the installation between the origin and the main distribution point of the installation
where further short-circuit protection is provided. |
|