是不允许 只有 单靠变频器起停的 泵吧
你是否想说:GB 27898.2-2011《固定消防给水设备 第2部分:消防自动恒压给水设备》,错了。 个人 觉得 消防系统 只有 单靠变频器起停的 消防泵 不合适, 若与 GB 27898.2-2011 冲突 以GB为准{:lol:} qsy 发表于 2015-12-28 16:11
个人 觉得 消防系统 只有 单靠变频器起停的 消防泵 不合适, 若与 GB 27898.2-2011 冲突 以GB为准
没人说过消防系统“ 只有 单靠变频器起停的 消防泵”。
若与 GB 27898.2-2011 冲突 以GB为准——
呵呵,麻烦了,人家 GB 50116-2013 也是 GB 标准哦。 这个GB 50116 历来就学不好 再来个-2013就更没法领会精神了。 qsy 发表于 2015-12-28 16:48
这个GB 50116 历来就学不好 再来个-2013就更没法领会精神了。
应该是:GB 50116-2013 不学好!
GB 50116-2013 自身稀里哗啦的,却对其他系统指手画脚。
试问丁大主编:人家消防水系统用不用变频泵,干卿何事? 当然,中国的工程看中国规范。
我只是想知道老美规范条文来由。 我的一位资深意大利设备工程师朋友的回答:
I hope that he can help you or at least try to.
Instead, concerning inverters on fire fighting pumps I do not know nfpa in detail as you do. In any case my idea is that you must be very careful because the fire system must be very simple and reliable in operation therefore in my opinion he vfd is not recommended because it can give troubles of reliability in the moment of need,which is always emergency. Also it would be interesting to know why you need the spèeed variation, this seems strange to me In any case for fire fighting. In Italy and Europe I have never seen a pumping station for ff with variable speed drive and personally I would never install one as per above. If you have a case in which you need very different pressures on various circuits it is better to use more than one pump group,each with the necessary pressure head on the specific circuit (I. E. Hydrants and sprinklers)
In any case you can try to ask angerame and maybe other suppliers of pumps. Consider that also for water mist the Marioff system works always with maximum flow ad has a system to bypass to the water tank all the flow that cannot go to system. Therefore this system creates a variable flow without any speed control.
Hope this is a good starting point for your needs, please do no hesitate to ask again if you need.
东海龙王 发表于 2015-12-29 08:19
我的一位资深意大利设备工程师朋友的回答:
I hope that he can help you or at least try to.
Instead,...
回答的很清楚,消防的时候为何要改变水泵的转速呢 taiyuntao 发表于 2015-12-29 08:45
回答的很清楚,消防的时候为何要改变水泵的转速呢
变频恒压,但用到的地方极为有限。 看来这个意大利人也不了解NFPA的这个变频水泵用在什么场合比较合适,可以认为NFPA只是不禁止使用并对如果使用提出限制条件,具体由设计根据实际工程考虑,可灵活运用。 呵呵,这个意大利老兄以为我在询问HI-FOG.高压细水雾当然不需要变频。
rainmen_73看的清楚。
页:
1
[2]