beaty 发表于 2009-6-21 00:03:17

嘿嘿嘿嘿 发表于 2009-6-21 11:35:13

回复:一有排烟多层宿舍楼做法

<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 18pt; mso-pagination: widow-orphan; mso-margin-top-alt: auto; mso-margin-bottom-alt: auto; mso-line-height-rule: exactly"><st1:chsdate w:st="on" Year="1899" Month="12" Day="30" IsLunarDate="False" IsROCDate="False">13.1.3</st1:chsdate>下列民用建筑应设置火灾自动报警系统:<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 18pt; mso-pagination: widow-orphan; mso-margin-top-alt: auto; mso-margin-bottom-alt: auto; mso-line-height-rule: exactly">1高层建筑:1)有消防联动控制要求的一、二类高层住宅的公共场所;2)建筑高度超过<st1:chmetcnv w:st="on" UnitName="m" SourceValue="24" HasSpace="False" Negative="False" NumberType="1" TCSC="0">24m</st1:chmetcnv>的其他高层民用建筑,以及与其相连的建筑高度不超过<st1:chmetcnv w:st="on" UnitName="m" SourceValue="24" HasSpace="False" Negative="False" NumberType="1" TCSC="0">24m</st1:chmetcnv>的裙房。<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 18pt; mso-pagination: widow-orphan; mso-margin-top-alt: auto; mso-margin-bottom-alt: auto; mso-line-height-rule: exactly">2、多层及单层建筑:<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 18pt; mso-pagination: widow-orphan; mso-margin-top-alt: auto; mso-margin-bottom-alt: auto; mso-line-height-rule: exactly">1)9层及9层以下的设有空气调节系统,建筑装修标准高的住宅;<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 18pt; mso-pagination: widow-orphan; mso-margin-top-alt: auto; mso-margin-bottom-alt: auto; mso-line-height-rule: exactly">2)建筑高度不超过<st1:chmetcnv w:st="on" UnitName="m" SourceValue="24" HasSpace="False" Negative="False" NumberType="1" TCSC="0">24m</st1:chmetcnv>的单层及多层公共建筑;<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 18pt; mso-pagination: widow-orphan; mso-margin-top-alt: auto; mso-margin-bottom-alt: auto; mso-line-height-rule: exactly">3)单层主体建筑高度超过<st1:chmetcnv w:st="on" UnitName="m" SourceValue="24" HasSpace="False" Negative="False" NumberType="1" TCSC="0">24m</st1:chmetcnv>的体育馆、会堂、影剧院等公共建筑;<o:p></o:p></P>
<P class=MsoNormal style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 24pt; LINE-HEIGHT: 18pt; mso-pagination: widow-orphan; mso-margin-top-alt: auto; mso-margin-bottom-alt: auto; mso-line-height-rule: exactly"><STRONG><FONT face=黑体><FONT size=1>4)设有机械排烟的公共建筑;</FONT></FONT></STRONG><o:p></o:p></P>

xuhui6512 发表于 2009-6-21 22:50:37

回复:一有排烟多层宿舍楼做法

<DIV class=quote>以下是引用 <B>beaty</B></FONT> 在(<I>2009/6/21 0:03:17</I>)的发言<BR>
<P>宿舍楼内走道超过40m,按规范应设置排烟,宿舍楼室外消防用水量未超过25,从照明总箱单独一路电源配电可以吗?</P>
<P>宿舍楼为设火灾自动报警系统,在每楼层排烟阀附近设手动按钮,火灾时能手动开启风机,屋面280度排烟阀动作时联动关闭排风机,</P>
<P>以上做法合理吗?</P></DIV>
<P>有自动报警系统,为什么仅要手动,火灾报警时,应自动打开排烟阀并联动排烟风机。自动失败时,用手动。</P>
<P><BR> </P>
页: [1]
查看完整版本: 一有排烟多层宿舍楼做法