关于新民规卫生间0 1 2 区划分问题紧急讨论
<P class=MsoList style="MARGIN: 0cm 0cm 0pt 21pt; TEXT-INDENT: -21pt"><STRONG><FONT color=#22dd22>新民规条文:</FONT></STRONG></P><P class=MsoList style="MARGIN: 0cm 0cm 0pt 21pt; TEXT-INDENT: -21pt"><FONT color=#0000ff><STRONG><FONT size=5>9开关和控制设备的装设应符合以下要求:</FONT></STRONG></FONT></P>
<P class=MsoBodyText style="MARGIN: 0cm 0cm 6pt"><FONT color=#0000ff><STRONG><FONT size=5>1)0、1及2区内,不应装设开关设备及线路附件;当在2区<FONT color=#ff0033>外</FONT>安装插座时,其供电应符合下列条件:</FONT></STRONG></FONT></P>
<P class=MsoListBullet style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 0cm; mso-char-indent-count: 0; mso-list: none; tab-stops: 21.0pt"><FONT color=#0000ff size=5><STRONG>——可由隔离变压器供电;</STRONG></FONT></P>
<P class=MsoListBullet style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 0cm; mso-char-indent-count: 0; mso-list: none; tab-stops: 21.0pt"><FONT color=#0000ff size=5><STRONG>——可由安全特低电压供电;</STRONG></FONT></P>
<P class=MsoListBullet style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 0cm; mso-char-indent-count: 0; mso-list: none; tab-stops: 21.0pt"><FONT color=#0000ff><STRONG><FONT size=5>——由剩余电流动作保护器保护的线路供电,其额定动作电流值不应大于30mA。</FONT></STRONG></FONT></P>
<P class=MsoListBullet style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 0cm; mso-char-indent-count: 0; mso-list: none; tab-stops: 21.0pt"><FONT color=#0000ff><STRONG><FONT size=5></FONT></STRONG></FONT> </P>
<P class=MsoListBullet style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 0cm; mso-char-indent-count: 0; mso-list: none; tab-stops: 21.0pt"><STRONG><FONT color=#1ae61a>新民规附录</FONT></STRONG></P>
<P class=MsoListBullet style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 0cm; mso-char-indent-count: 0; mso-list: none; tab-stops: 21.0pt"><FONT color=#0000ff size=5><STRONG>1区的界限是:围绕浴盆或淋浴盆的垂直平面,或对于无盆淋浴,距离淋浴喷头1.2m的垂直平面和地面以上0.1m至2.25m的水平面 </STRONG></FONT></P>
<P class=MsoListBullet style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 0cm; mso-char-indent-count: 0; mso-list: none; tab-stops: 21.0pt"><FONT color=#0000ff size=5><STRONG>2区的界限是:1区外界的垂直平面和与其相距0.60m的垂直平面,地面和地面以上2.25m的水平面。</STRONG></FONT></P>
<P class=MsoListBullet style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 0cm; mso-char-indent-count: 0; mso-list: none; tab-stops: 21.0pt"><FONT color=#0000ff size=5><STRONG></STRONG></FONT> </P>
<P class=MsoListBullet style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 0cm; mso-char-indent-count: 0; mso-list: none; tab-stops: 21.0pt"><STRONG><FONT color=#f70938>这样的话设置淋浴喷头的卫生间(无隔板) </FONT></STRONG></P>
<P class=MsoListBullet style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 0cm; mso-char-indent-count: 0; mso-list: none; tab-stops: 21.0pt"><STRONG><FONT color=#f70938>插座要装到2区以外,就要距离淋浴喷头垂直平面1.8米以外的距离</FONT></STRONG></P>
<P class=MsoListBullet style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 0cm; mso-char-indent-count: 0; mso-list: none; tab-stops: 21.0pt"><STRONG><FONT color=#f70938>这个对于面积较小的卫生间是很难达到要求的!</FONT></STRONG></P>
<P class=MsoListBullet style="MARGIN: 0cm 0cm 0pt; TEXT-INDENT: 0cm; mso-char-indent-count: 0; mso-list: none; tab-stops: 21.0pt"><FONT color=#0000ff><STRONG></STRONG></FONT> </P>
回复:关于新民规卫生间0 1 2 区划分问题紧急讨论
<P>卫生间小,就装卫生间外(热水器插座装2.25米以上);一般除热水器外,其他插座用的机会也少。</P>回复:关于新民规卫生间0 1 2 区划分问题紧急讨论
新老民规在这一点上并没有太大的变化<BR>回复:关于新民规卫生间0 1 2 区划分问题紧急讨论
说没有太大变化的拿新老规范对比一下吧,区别很不小的。当然了有这个改变也是由于IEC的规范2006年修订了回复:关于新民规卫生间0 1 2 区划分问题紧急讨论
<P>老民规条文:</P><P>14.8.2.8 在0、1及2区内,不允许非本区的配电线路通过;也不允许在该区内装设接线盒。<BR>14.8.2.9 开关和控制设备的装设,须符合以下要求:<BR>(1)在0、1及2区内,严禁装设开关设备及辅助设备。在3区内如安装插座,必须符合以下条件才是允许的: <BR>a.由隔离变压器供电。<BR>b.由安全超低压供电。<BR>c.由采取了漏电保护措施的供电线路供电,其动作电流I△n值不应超过30mA。</P>
<P>老民规附录:</P>
<p>1区的界限是:围绕澡盆或淋浴盆的垂直平面,或对于无盆淋浴,距离淋浴喷头0.6m的垂直平面,和地面和地面至上2.25m的水平面 <BR>
<P>2区的界限是:1区外界的垂直平面和和1区之外0.60m的平行垂直平面,地面和地面以上2.25m的水平面。</P>
回复:关于新民规卫生间0 1 2 区划分问题紧急讨论
我在想:外国人的卫生间是不是比我们的要大些?
页:
[1]