AIEN1119 发表于 2020-12-28 16:53:20

照明导线根数确定

data:image/gif;base64,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

如图照明导线,哪些导线根数需要标注,有没有大牛解释一下,标注一下

geniushzw 发表于 2020-12-28 16:57:28

你这个需要找个师傅手把手教你。。

AIEN1119 发表于 2020-12-28 16:58:45

geniushzw 发表于 2020-12-28 16:57
你这个需要找个师傅手把手教你。。

大佬标注一下呗{:1_428:}

AIEN1119 发表于 2020-12-28 17:03:03

geniushzw 发表于 2020-12-28 16:57
你这个需要找个师傅手把手教你。。

请问我这样标对吗

贾行家 发表于 2020-12-28 17:10:46

3根居多,所以3根就不标了,未标注的就都是3根。

AIEN1119 发表于 2020-12-28 17:12:28

贾行家 发表于 2020-12-28 17:10
3根居多,所以3根就不标了,未标注的就都是3根。

唉,刚做电气设计,我就是不清楚根数,大佬,你看看我4楼标的对吗?

AIEN1119 发表于 2020-12-28 17:18:56

贾行家 发表于 2020-12-28 17:10
3根居多,所以3根就不标了,未标注的就都是3根。

那您看看,如果我多增一个控制的灯,原来三根的导线是不是应该多加一个控制线,这样对吗?

x01oct 发表于 2020-12-28 22:14:46

本帖最后由 x01oct 于 2020-12-28 22:20 编辑

几根需要标注,几根不需要标注,需要设计人员自己来定义。
我通常习惯PE线不标,只标其余的线。

但是我这里有人习惯把线根数都算上,3根的不标。我不喜欢这样的标法。

x01oct 发表于 2020-12-28 22:19:47

AIEN1119 发表于 2020-12-28 17:18
那您看看,如果我多增一个控制的灯,原来三根的导线是不是应该多加一个控制线,这样对吗?

多加的一根是电源线,不是控制线

不代表 发表于 2020-12-29 07:58:57

3根及3根以下不标了,不然标太多了

百家钱 发表于 2020-12-29 08:48:41

我就没标过....

AIEN1119 发表于 2020-12-29 08:56:34

x01oct 发表于 2020-12-28 22:19
多加的一根是电源线,不是控制线

好,谢谢大佬{:1_428:}

x01oct 发表于 2020-12-29 09:24:23

不代表 发表于 2020-12-29 07:58
3根及3根以下不标了,不然标太多了

应该只有一种不标,而不是有2种都不标

轻云舟 发表于 2020-12-29 10:28:17

我觉得第二张图中间的4应该是3,就是相当于从配电箱出来的零火地三根线,其他的标的都对。画个初中的图就能看明白

CLOCK 发表于 2021-1-5 11:15:50

去看看装修的屋穿线视频,你就明白了。
页: [1] 2